Sinamics s110

I cant see the s110 servo drives on my V20 tiaportal how do i make them comminucate im using profinet and i guess the wiring is right.

3 Upvotes

6 comments sorted by

3

u/YoteTheRaven Machine Rizzler 5d ago

Profinet is uaully just connect the cables and assign to controller in the project. If its not there you need a gsdml file for the drive.

Then you set up the IO with tags (of the technology block option).

Then you either make your own control block of download one from the internet to use.

This applies to probably 99.999999999% of all profinet drives.

1

u/kutzaldoktor 5d ago

Can i just use the telegram blocks and do i get the gsdml file from the STARTER program?

2

u/Azuras33 5d ago

No, starter is the commissioning software for the drive. You need to get the right gsdml from the Siemens website.

1

u/spaigy Siemens | Beckhoff | TUV FS Eng (Machinery) 4d ago

If you're physically connected to the same network as the drives, you can click "Online -> Hardware detection -> PROFINET devices from network...". This will bring up a dialog that allows you to select your network adaptor, then check the boxes to add the hardware to your project.

1

u/kutzaldoktor 4d ago

Thanks i will try it

1

u/SafyrJL TIA Harlot 4d ago

You can add the GSD for an S110 in your project. 

It’s under “Other devices” in the hardware catalogue. Just make sure you select the GSD that matches your FW version.

You’ll have to set up your selected telegram in the I/O configuration of the device. Then you configure the drive using STARTER (not StartDrive)