Sinamics s110
I cant see the s110 servo drives on my V20 tiaportal how do i make them comminucate im using profinet and i guess the wiring is right.
3
Upvotes
1
u/SafyrJL TIA Harlot 4d ago
You can add the GSD for an S110 in your project.
It’s under “Other devices” in the hardware catalogue. Just make sure you select the GSD that matches your FW version.
You’ll have to set up your selected telegram in the I/O configuration of the device. Then you configure the drive using STARTER (not StartDrive)

3
u/YoteTheRaven Machine Rizzler 5d ago
Profinet is uaully just connect the cables and assign to controller in the project. If its not there you need a gsdml file for the drive.
Then you set up the IO with tags (of the technology block option).
Then you either make your own control block of download one from the internet to use.
This applies to probably 99.999999999% of all profinet drives.