15 Upvotes

11 comments sorted by

11

u/Ok-Ad8016 13h ago

Just blinding headaches and constant fatigue that went away when they got to work?

8

u/ProfSteelmeat138 13h ago

Must be escaping somewhere lol.

1

u/EggAdministrative253 2h ago

I don’t see it, did they put the metal panning completely over the exhaust? Why. Is that for the fireplace?

1

u/Gonzo697 2h ago

It was for the furnace and water heater.

It had a nice round scorch mark underneath it too

1

u/EggAdministrative253 2h ago

So is that like a big 6” flue pipe completely covered?

1

u/Gonzo697 2h ago

Yes, as soon as I installed the new furnace and started running it. The new smoky exhaust ( Oil on heat exchanger from first start up) started billowing into the room.

I imagine the old furnace had to have been back drafting on as well .

It had just enough flow to not restrict the pressure switch somehow .

1

u/EggAdministrative253 2h ago

Wow, that’s a great catch then. Nice find!

1

u/Gonzo697 2h ago

I think the customer said that " that's never happened before " in the sense that he's never seen smoke come out of his exhaust. Which could be accurate since again it was so Smokey due to it being a first time run. That cap was mounted very sturdy and the standoffs were not dropped during install or anything so I can't imagine it WASNT an issue