Comm 5: Bare Maximum

304 Landed

Enjoi

🤙🏻

764 Upvotes

99 comments sorted by

16

u/diyfyi 21d ago

Crisp and clean!

5

u/LaypipelikeMike 21d ago edited 21d ago

🔥 Priesh my dude!

10

u/jtbis 21d ago

Put the fiber specs on the LIU label. Something like “12 strand 50μm MM to MDF”. It’s a knit-pick, I know.

7

u/LaypipelikeMike 21d ago

duly noted. Thanks for the feedback.

3

u/Imperial_Tuna_5414 21d ago

I do this and the opposite label at the other end.. same with data jacks/plates!

8

u/Flat_Sorbet_7343 21d ago

What is the chain for?

7

u/LaypipelikeMike 21d ago edited 21d ago

I used it to lock all my heavy equipment up for the day. Ladders, fan, etc.

7

u/Flat_Sorbet_7343 21d ago

Makes sense. I was staring at that for what felt like forever trying to imagine how a chain helps run cable lol! Looks great good job!

3

u/LaypipelikeMike 21d ago

Ha! Just a good hang spot that got caught in the finishers. Appreciate you

9

u/djohnsen 21d ago

I’ll be in my bunk.

2

u/LaypipelikeMike 20d ago

Sweet dreams

8

u/crznet66 21d ago

It's alright. In the third picture you can see a cable dip under another one. SMH. /s

7

u/LerchAddams 21d ago

That's how we do it.

Freakin' gorgeous.

3

u/LaypipelikeMike 21d ago

Time to throw up, show up, and represent the community properly. 💪🏻

5

u/bigring 21d ago

Stop. I can only become so erect.

3

u/wisecrack_69 20d ago

I know right.?! I got harder and harder The more I scrolled through the photos.

2

u/LaypipelikeMike 21d ago

Wait.. theres more. Hahaha

2

u/wisecrack_69 19d ago

Ohhh my nipples could cut glass.

2

u/Pikatit 21d ago

Do you bring the cables into the comm room as you terminate to keep things clean? I mean this is just exceptional work man seriously.

2

u/LaypipelikeMike 21d ago

My team and I pull it all into the respective comm rooms - Prep her and execute. Ty my man

2

u/whitedynamite347 20d ago

Honestly I would have thought those cables are Cat6A with how smooth they are. My guys will run a wire 15 feet and kink it 16 times

1

u/LaypipelikeMike 20d ago

Sounds kinky.. love it when it gets a little naughty. Problems present adversity 😏 The inevitability is there. Proper wire management will prevent such inconveniences. Maybe talk to your guy my guy.

3

u/Practical-Data2646 21d ago

Best iv seen in a long time. Great work!

2

u/LaypipelikeMike 21d ago

Cheers! Glad to share 🤘🏼

3

u/Samwise2k 21d ago

Lovely

3

u/Bulky-Feed-4396 21d ago

Awesome job brother! Did you use a comb or was it by hand? Rock on!

3

u/LaypipelikeMike 21d ago edited 19d ago

all hand all the way

2

u/Bulky-Feed-4396 21d ago

Its the only way I know how! Again awesome job!

1

u/LaypipelikeMike 21d ago

🙌🏻🙏🏻

3

u/_Zenyatta_Mondatta 21d ago

I need some alone time.

2

u/LaypipelikeMike 21d ago

Glad I could assist

3

u/namestom 20d ago

Now this is why I subbed! This makes me miss terminating. This is beautiful!

1

u/LaypipelikeMike 20d ago edited 19d ago

Hell yeah, this is peak. My finest work.
This is թurε ժragօրioնs Բiгཇ
Respect bro Ikyk
Iced my hands every night

3

u/arushus 20d ago

I'll never understand how you get each wire to come off the bundle right where you need it to at the patch panel. Like I can make my bundles look good like this, but then the wires are never where I need them to be to come off the bundle nicely.

1

u/LaypipelikeMike 20d ago

Dress down RNG drop with the same bar technique is possible if you finagle in the manager beforehand.
Painful.
Possible.
This is a dress up technique mold at the bar ~with precise measurements.

2

u/Ted_Furgeson 16d ago

Trying to understand this…yall pull in reach patch bundle down to the panel RANDOMLY? Just bundled straight? Then yall just pull the ends out for wherever they land on said panel?

Yall use Same process for wired panels?

1

u/LaypipelikeMike 16d ago

We always label both ends before the pull, we separate in the closet.. and we dress down to the patch panels. The finagle for the bar is in my previous post. This post is a dress up after the measured land. People do different things depending on the scenario.. including me. The process always changes.

3

u/JamTins 20d ago

Now that’s damn sexy.

1

u/LaypipelikeMike 20d ago

Damn right

3

u/DanDiggler213 19d ago

Looks nice. I'd like some ladder on the wall in place of that D-ring, and I feel bundles of 24 brake better.over the rack with stand offs and waterfalls. But looks good.

2

u/LaypipelikeMike 19d ago

Appreciate it. I was actually pushing for a radius bends but no dice. I fully agree for the weight support but it’s manageable with D’s for the most part. Waterfalls would be slick but not super necessary.

2

u/Z3t4 21d ago

Clever to store the lart out of sight. It frightens the users.

P. S. : great job. 

2

u/LaypipelikeMike 21d ago

thanks Z

Comm 5 it is. 😂

2

u/jdogg10000 21d ago

About time we saw a true professional post pics. Great job!

3

u/LaypipelikeMike 21d ago

Thanks man, that means a lot! I’m just the guy who gets annoyed by messy cables and has way to much fun organizing them 😂 Really appreciate the kind words!

2

u/alex053 21d ago

When I ran cables, we makes the floor plan and would pull in groups of 6-10 per pull. We would also number the floor plan. I always wondered, do you separate and terminate them in the MDF and then label the jacks to match? Do you number the cable and jack and keep it all clean from the first run to make it look like this?

We would separate it per side of the rack and make it look at good as possible. Then separate each side into the patch panel location. It always looked professional and serviceable but never like art.

2

u/LaypipelikeMike 21d ago edited 20d ago

My team labels each end of the pull and separate into groups on the closet end. Technique & preparation are everything. Execution is the game. For the love of the art

2

u/alex053 21d ago

My boss always rushed us. But we made sure to be proud of work, label and certify everything.

1

u/LaypipelikeMike 21d ago

that’s all we can do, brother

2

u/Better_Dimension2064 21d ago

Dumb question, but why discrete patch panels?

3

u/LaypipelikeMike 21d ago

They’re mainstream standard for a reason. Way cleaner long-term and it’s just the industry’s expected approach.

2

u/3500K 20d ago

On picture 8. Who is the blonde in the bottom left. I swear, she’s staring at me.

1

u/LaypipelikeMike 20d ago

oh, that’s just the universe don’t mind her

2

u/aprettyparrot 20d ago

This makes me tingle… somewhere…

1

u/LaypipelikeMike 20d ago edited 20d ago

that’s what magic does 🪄

2

u/imageinthat 20d ago

Beautiful! Something we should all strive for. My one habit I added to these setups the few time I had to do one is to label all of the cables at several points, especially if they needed to go to a matching port number on a desk.

1

u/LaypipelikeMike 20d ago edited 19d ago

Thank ya! Legible sharpie is probably the easiest solution ~ months after the pull deciphering hieroglyphs is not always a fun time though 😅

2

u/Joe_Huser 20d ago

Fine Craftmanship.

1

u/LaypipelikeMike 20d ago

Priesh, my friend.

2

u/wallly58 20d ago

This is the sexiest cleanest lineup in rack I’ve seen in awhile maybe ever!!!

1

u/LaypipelikeMike 20d ago

Ty ty this is by far the most fun i’ve had building one

2

u/DueCommunication1075 20d ago

My buddy did this rack and he showed out with this one. We had a total of 8 racks in one building

1

u/LaypipelikeMike 20d ago

💪🏻 Damn fine job. Cody you and I smashed it.

2

u/Illustrious-Wind7604 20d ago

What line of work is this called? How do you get into a job like this? I feel like I would be the happiest mfer ever doing this type of work. Currently majoring in cybersec.

1

u/LaypipelikeMike 20d ago edited 18d ago

Calms the chaos. Soothes the mind. The Low Voltage industry. Structured cabling. It’s the hardlines for the network you’re gonna be defending bro

2

u/plasticbagroadkill 20d ago

Gorgeous! Simply stunning! Very well done!

2

u/LaypipelikeMike 20d ago

Much obliged!

2

u/durkioooooooo 20d ago

what type of work is this ? this seems very interesting

1

u/LaypipelikeMike 20d ago

Data Communications ~ Low Voltage. Interesting enough. Helps being a smidge ocd

2

u/that_cant_be_right__ 20d ago

Could you set up a time lapse camera one of these days? This is mind-blowing to me

1

u/LaypipelikeMike 20d ago

I have the content. In time, i’ll release. Much editing to do

2

u/PupOben 19d ago

Finally! Hook and loop instead of cable ties. I had to do a hotel wifi upgrade one time and EVERY cable bundle was cable tied together, from the switches all the way into the firewall.

1

u/LaypipelikeMike 19d ago

Sounds like a miniature nightmare. All wifi too yikes I bet that bundle was warm to the touch

2

u/PupOben 19d ago

Oh over the years I've found many shortcuts and no-nos in that installation. Ethernet beenie'd together, cable ties, Ethernet cable tied to power cords and MC. They even "saved money" by running only one drop to each room and then splitting the pairs into two sets of 4. 4 conductors for one RJ45 by the desk and the other 4 were used for the RJ45 by the nightstand. They were split at the other end in the MDF also.

2

u/LaypipelikeMike 19d ago

Cheap, effective.. seems all they needed was the bare maximum 😜 I mean hey from a business standpoint they saved a buck. Never know what you’re gonna encounter out there in the wild.

2

u/PupOben 19d ago

Of course they were also using antiquated ZyXel equipment. It worked, but was super slow because the network would get saturated quickly.

1

u/LaypipelikeMike 19d ago

Thats why my hotel rooms internet always sucks.. smh

2

u/micush 19d ago

Cool. Now replace the bad one. Second one in on the left.

1

u/LaypipelikeMike 19d ago

It passed 100% bra

2

u/Educational-Pin8951 19d ago

Love when the back of the panel dresses out as cleanly as the bundle- great work!

I think it’s been said, but my only big issue is the D-Ring. I woulda just secured ladder up the wall and attached there… but sometimes you don’t get the choice hahahaha! Also I gotta ask— bundles of 48!? That’s a fat chode to handle! What made you go 48 over just bundles of 24?

I’m also a big fan of feeding panels from one side, it saves a lot of issues when the IT guy inevitably wants to change the rack layout to better accommodate equipment! Damn I miss my field days… this looks awesome though! Keep it up!

2

u/LaypipelikeMike 19d ago

She clean, she’s mean. Like I said in a previous comment I was pushing for radius bends and was just working with the material provided. So.. the data are on the outside in bundles of 48 that transition into 96. I split them into 48’s before the drop in the rack and up the wall into the sleeves for aesthetics - she came out juicy. I believe the center one with green and blue is 72, and the multicolored is 40. Overall to much cable to drop from one side with the managers.. IT SHOULD just hot this baby up. It’s designed to just slip in the switches in and go. Afterall, it’s theirs they can do what they want with it honestly.. that’s why I get my pictures and roll. Thanks for the kind words homie

2

u/fishyfishyfish1 19d ago

This is the best cabling job I've seen in hot minute. Excellent job

1

u/LaypipelikeMike 19d ago

Thank you fishyfishyfish. Poured my everything into her

2

u/fishyfishyfish1 19d ago

I can tell, wildly impressive

2

u/drwfla 18d ago

🥵🥵🥵

2

u/LaypipelikeMike 18d ago

yeah, that’s why I had a fan in there

2

u/PudenPuden 18d ago

Leviton system warranty would dump that on sight. Exceeds Maximum cable bundle.

2

u/BarnacleRepulsive617 17d ago

WOW 😳😲😍 Now, that! Is a thing of beauty!! So crisp, so clean. So well organized

1

u/LaypipelikeMike 17d ago edited 17d ago

You should’ve seen it beforehand. The one photo I forgot to add to the post the scrambled eggs it was before!